Resources:
http://www.iccsafe.org/GR/Pages/adoptions.aspx
http://en.wikipedia.org/wiki/Interna..._Building_Code
http://www.standard-building-code.com/boca-codes.shtml (buy a copy of the book) (look up special amusement / haunted houses)
http://www.nfpa.org/itemdetailjourna...6&itemID=36230 (article about haunted houes which states the following rules for haunted houses) (what does it say about a haunted house and sprinkler systems... read on) No bully tactics just facts! You wanted facts here they are ... clear as day.
patrons an additional tool to assist them in finding their way out under emergency conditions.
Special amusement buildings
Chapter 12 Section 12.4.7 and Chapter 13, Section 13.4.7 are identical, deal with the life-safety requirements for Special Amusement Buildings, and state the following:
12/13.4.7.1* General. Special amusement buildings, regardless of occupant load, shall meet the requirements for assembly occupancies in addition to the requirements of 12/13.4.7, unless the special amusement building is a multilevel play structure that is not more than 10 feet (3,050 millimeters) in height and has aggregate horizontal projections not exceeding 160 feet2 (15 meters2).
12/13.4.7.2* Automatic Sprinklers. Every special amusement building, other than buildings or structures not exceeding 10 feet (3,050 millimeters) in height and not exceeding 160 feet2 (15 meters2) in aggregate horizontal projection, shall be protected throughout by an approved, supervised automatic sprinkler system installed and maintained in accordance with Section 9.7.
12/13.4.7.3 Temporary Water Supply. Where the special amusement building required to be sprinklered by 12/13.4.7.2 is movable or portable, the sprinkler water supply shall be permitted to be provided by an approved temporary means.
12/13.4.7.4 Smoke Detection. Where the nature of the special amusement building is such that it operates in reduced lighting levels, the building shall be protected throughout by an approved automatic smoke detection system in accordance with Section 9.6.
12/13.4.7.5 Alarm Initiation. Actuation of any smoke detection system device shall sound an alarm at a constantly attended location on the premises.
12/13.4.7.6 Illumination. Actuation of the automatic sprinkler system, or any other suppression system, or actuation of a smoke detection system having an approved verification or cross-zoning operation capability shall provide for the following:
(1) Increase in illumination in the means of egress to that required by Section 7.8
(2) Termination of any conflicting or confusing sounds and visuals
12/13.4.7.7 Exit Marking.
12/13.4.7.7.1 Exit marking shall be in accordance with Section 7.10.
12/13.4.7.7.2 Floor proximity exit signs shall be provided in accordance with 7.10.1.6.
12/13.4.7.7.3* In special amusement buildings where mazes, mirrors, or other designs are used to confound the egress path, approved directional exit marking that becomes apparent in an emergency shall be provided.
12/13.4.7.8 Interior Finish. Interior wall and ceiling finish materials complying with Section 10.2 shall be A throughout.
http://www.iccsafe.org/GR/Pages/adoptions.aspx
http://en.wikipedia.org/wiki/Interna..._Building_Code
http://www.standard-building-code.com/boca-codes.shtml (buy a copy of the book) (look up special amusement / haunted houses)
http://www.nfpa.org/itemdetailjourna...6&itemID=36230 (article about haunted houes which states the following rules for haunted houses) (what does it say about a haunted house and sprinkler systems... read on) No bully tactics just facts! You wanted facts here they are ... clear as day.
patrons an additional tool to assist them in finding their way out under emergency conditions.
Special amusement buildings
Chapter 12 Section 12.4.7 and Chapter 13, Section 13.4.7 are identical, deal with the life-safety requirements for Special Amusement Buildings, and state the following:
12/13.4.7.1* General. Special amusement buildings, regardless of occupant load, shall meet the requirements for assembly occupancies in addition to the requirements of 12/13.4.7, unless the special amusement building is a multilevel play structure that is not more than 10 feet (3,050 millimeters) in height and has aggregate horizontal projections not exceeding 160 feet2 (15 meters2).
12/13.4.7.2* Automatic Sprinklers. Every special amusement building, other than buildings or structures not exceeding 10 feet (3,050 millimeters) in height and not exceeding 160 feet2 (15 meters2) in aggregate horizontal projection, shall be protected throughout by an approved, supervised automatic sprinkler system installed and maintained in accordance with Section 9.7.
12/13.4.7.3 Temporary Water Supply. Where the special amusement building required to be sprinklered by 12/13.4.7.2 is movable or portable, the sprinkler water supply shall be permitted to be provided by an approved temporary means.
12/13.4.7.4 Smoke Detection. Where the nature of the special amusement building is such that it operates in reduced lighting levels, the building shall be protected throughout by an approved automatic smoke detection system in accordance with Section 9.6.
12/13.4.7.5 Alarm Initiation. Actuation of any smoke detection system device shall sound an alarm at a constantly attended location on the premises.
12/13.4.7.6 Illumination. Actuation of the automatic sprinkler system, or any other suppression system, or actuation of a smoke detection system having an approved verification or cross-zoning operation capability shall provide for the following:
(1) Increase in illumination in the means of egress to that required by Section 7.8
(2) Termination of any conflicting or confusing sounds and visuals
12/13.4.7.7 Exit Marking.
12/13.4.7.7.1 Exit marking shall be in accordance with Section 7.10.
12/13.4.7.7.2 Floor proximity exit signs shall be provided in accordance with 7.10.1.6.
12/13.4.7.7.3* In special amusement buildings where mazes, mirrors, or other designs are used to confound the egress path, approved directional exit marking that becomes apparent in an emergency shall be provided.
12/13.4.7.8 Interior Finish. Interior wall and ceiling finish materials complying with Section 10.2 shall be A throughout.